Heat loss: how big a heat pump does a house need?

2 min read · self-test time extra

A heat pump is sized from how much heat the house loses on a cold day, room by room, not from the size of the old boiler.

Have a go

Heat pumps0 in a row0 XP

Which is a fabric-loss path?

Tap an answer

Two ways heat escapes

Heat leaks out through the walls, roof, floor and windows: that's fabric loss. It's also carried away by air leaving the house and being replaced by cold air: that's ventilation loss. A heat loss calculation adds both up for every room.

One wall, worked through

Fabric loss is the U-value times the area times the temperature difference. A wall with a U-value of 0.4 W/m²K, 15 m² in area, with 20 °C between inside and out, loses 0.4 × 15 × 20 = 120 W. Do that for every surface in every room.

The design day

The calculation uses a cold outdoor design temperature for the location and a target temperature for each room. The MCS design standard, MIS 3005-D, points to the BS EN 12831-1 method; a simple air-change sum is a way to learn the idea, not the full method.

Why bigger isn't better

Rooms are matched first, then the building's total sets the heat pump. A unit much bigger than the loss switches on and off too often, which is called short cycling, and that wastes energy and wears the compressor.

Key numbers

120 W
A 15 m² wall at U = 0.4 W/m²K with a 20 °C difference: 0.4 × 15 × 20.

Common mistakes

  • Sizing the heat pump to match the old boiler's output.
  • Adding up the whole house without checking each room can be heated.
  • Forgetting ventilation loss and counting the walls and windows only.

The lessons this guide comes from

  • Where a house loses heat
  • Fabric heat loss
  • Ventilation loss and design temperatures
  • Room-by-room assessment and sizing